Alwayslearningelec
- NJ
- Estimator
Can you have FUSED 200A switch feeding load with #8 wire? Doesn't wire need to be rated ampacity to match switch size?
AC unit with VFD and disconnectProbably not but what kind of breaker and what kind of load?
Conductors have to be sized to 125% of the input current of the VFD. With a 200 amp OCPD I doubt that #8 is the correct size.AC unit with VFD and disconnect
Question is what's the input current. Don't know.Conductors have to be sized to 125% of the input current of the VFD. With a 200 amp OCPD I doubt that #8 is the correct size.
No way for you to know without more input (RFI) or on-site inout BUT as noteds, with a 50 amp wire and 430.122 it's practically impossible that it would meet Code unless it'sa tap to another OCP device and meets 240.21Question is what's the input current. Don't know.