Question
hhsting
Glen bunie, md, us
Junior plan reviewer
Calculated demand load comes to 122A. The breaker used is 125A.
Would the cable size be 1/0 awg Al or 2/0 awg Al at 75C? I think its 1/0 awg Al but engineer says 2/0 awg Al should be the size
augie47
Tennessee
If it meets the requirement of 310.15(B)(7) then 1/0. If not, 2/0
Why do you think 1/0 ?
d0nut
Omaha, NE
Why do you think 1/0 would be acceptable at 75C?
Also, if this is under your work as a plan reviewer, why would you care if the conductors were upsized?
augie47
Tennessee
Two reasons:
1. NEC 2017 section 240.4(B)
Not applicable in this case. You have a 122 amp load so your conductor must be rated at at least 122 amps 215.2
2. I am not sure but this is five stories building with dwelling units. Would 310.15(B)(7) apply? Is it multi family dwelling unit?
If it's a dwelling unit, 310.15(B)(7) applies
hhsting
Glen bunie, md, us
The cable is feeding 208/120V three phase panelboard.
I am confused by 310.15(b)(7) as to how it applies? Would it apply even if its 5 stories building with dwelling units? Also how would it apply to three phase?
augie47
Tennessee
Do restaurant menus confuse you :)
For one-family dwellings and the individual dwelling units of two-family and multifamily dwellings, single-phase feeder conductors consisting of 2 ungrounded conductors and the neutral conductor from a 208Y/120 volt system shall be permit‐ ted to be sized in accordance with 310.15(B)(7)(1) through (3).
sounds like it is a dwelling unit in a multi-family dwelling so at that point it meets the requirements BUT, now that you added info (Sting SOP) that it is a 3 phase feeder it does not meet the requirement .... so 2/0 !
don_resqcapt19
Illinois
retired electrician
Please try reading all of the words in the section that you have cited. The code language in that section very clearly answers your questions.