I have 2 questions for fire pumps.
if you have one 2000 amp service switch feeding a building, plus a tap before this service switch to feed a fire pump... let's assume it's a 400 amp disconnect switch to feed the fire pump... is this considered a 2000 amp service or a 2400 amp service? I don't know if the fire pump switch is included.
The service entrance conductors to which the fire alarm tap is connected to... those service entrance conductors are sized at 125% of the continuous load, plus 100% of the non-continuos load, plus motor loads... plus 125% of the fire pump current? is the fire pump current included? Not sure if when the fire pump is on, all other loads might be off, or do you count as everything being on?