WA_Sparky
Electrical Engineer
- Vancouver, WA, Clark
- Electrical Engineer
Project I'm working on has the meter and main service disconnect (120/240V 1Ø service) out on the power pole on site. This panel serves (3) sub panel, (1) 200A 120/240 1Ø panel inside, (1) 125A 120/240V 1Ø sub panel on the same pole as service meter, and (1) 100A 120/240V 1Ø sub panel on a different pole.
The main service disconnect and the panel inside the building and the service disconnect both are using 4pole breakers as disconnects.
Can anyone explain why someone would use 4 pole disconnects? I remember running into this on a previous project with a generator that served multiple buildings due to multiple neutrals needing disconnected. Is 4p disconnect because the other loads on site arent connected to the buildings neutral/ground? I see why there would be a need for the 4p at the service but I cant wrap my head on why there would be a 4p disconnect for the Main on the panel inside?
Thanks,
Thanks,