Temp adj.
Alwayslearningelec
NJ
Estimator
If you have conduit and wire ran outdoors(where temp fluctuates throughout year bet 30deg and 95deg F) for an extended length say 300’ , do you need to adjust conductor ampacity? If so how would you do that with unknowns such as weather? Thanks
Temperature is always a consideration no matter the length of conductors and may require de-rating depending on your calculation of temperatures applicable. Conductor length consideration of voltage drop also might come into play. Look at Article 310 for the calculations criteria.
Given the parameters in the OP with 90° C conductors I think you can pretty much ignore any corrections.
However, that would require THHN-2 or XHHW-2 THHN/THWN would require using the 75 degree table because it is a wet location.
That's correct. I think that we're getting to the point where any new conductor will have 90°C wet or dry insulation.