Hey guys I’m sure there is a thread on this but I can’t find one. We are installing a service on a commercial building and the llord wants 4 200A Meters installed. The meter stack we are using Schneider MPH64200 has factory dual lugs that accommodate up to (2) 600 AL. They do not make anything bigger then that for their meter packs. They informed me that their buss is only rated for 600A and that is why they do not make bigger lugs then that. We sized the service for 700AL x 2 but now after talking with them, I’m a little lost on how we should go about sizing these cables. I feel this is a similar situation to a 320A meter with (2) 200A Panels ran off it…… but I could be wrong and I don’t want to be wrong with this one lol. Should we size these cables based on the busses of this meter ?? Any input would be appreciated. Thank you