Back-up Portable Generator grounding requirements for residential applications
JELECT.
New User
New York State
Elactrician
What are the grounding, bonding, and grounding electrode NEC requirements, regarding the use of a portable generator used for back-up power to a residential home? this generator would be plugged into a 30 amp 125/250 volt 4 wire male inlet which connects to the main panelboard through a manually operated 30 amp, 2-pole circuit breaker that can only be closed by opening the main 100 amp service breaker which is mechanically interlocked with 30 amp breaker?
That’s a lot to ask, it’s in Art 250 under generators, and article 702.
Is the generator solidly bonded or a floating neutral?
Actually a 3 pole transfer switch for most residences since they are single phase. The requirement is to switch the ungrounded and neutral conductors on a bonded generator, and use a 3 wire feed. It may need a GEC too. For an unbonded generator, you don't switch the neutral and use a 4 wire feed.
Please review section 702.7
The generator type, unbonded or bonded neutral, is matched to the type of transfer switch. Most generators are bonded neutral type. On a generator with gfci for its outlets, when used with a transfer switch that does not transfer the neutral, the gfci will trip.