Space from bus to enclosure

Status
Not open for further replies.

fatuus

Member
Location
Virginia
Occupation
Electrician
Good morning. I think NEC is silent regarding clearance requirements from bus to the enclosure. The same standard would apply to bolted connections. In other words, a compression lug is terminated to the gear. Bolt is facing outward. Is there a required distance from the bolt to the cover? Thank you for the help.
 
Good morning. I think NEC is silent regarding clearance requirements from bus to the enclosure. The same standard would apply to bolted connections. In other words, a compression lug is terminated to the gear. Bolt is facing outward. Is there a required distance from the bolt to the cover? Thank you for the help.
I don't know if the NEC has any requirements but ul508a does
 
seems to be in the construction specifications section, so would not seem to apply to field work.
While it probably does not apply to field work, the electrons do not care who installed the conductive parts. If those spacings are safe for the construction of the panelboard, they should also be safe for field installed conductive parts.
 
While it probably does not apply to field work, the electrons do not care who installed the conductive parts. If those spacings are safe for the construction of the panelboard, they should also be safe for field installed conductive parts.
The numbers certainly seem more than adequate.
 