tamiya0603
- calgary, Canada
- Electrical Engineer
Hello there,
I am new to the forum and are looking for help or opinion on the issue below from fellow electrical folks.
I have encountered a design issue with installing a 100A disconnect switch for a cooling fan application. The system is 3PH, 480V, Fan motor is 50HP 45FLA, it take about 3 sec for the fan to fully start and back to normal operating FLA. During the 3 sec inrush, we will see 240A. The 100A switch is installed near fan motor for isolation use only. during operation switch will stay closed and locked. Switch model number is a Westinghouse DS36U, based on datasheet it's rated for 75HP at 480V. i would think since switch is 75HP rated and it should withstand 75HP motor inrush. but most motor inrush last only about 1 sec, in our case the fan is taking longer about 3 sec to pick up full speed. there is no catalogue information mentioning inrush current rating or withstand durations.
I checked the UL98 standard of the switch also didn't mention anything about motor inrush. the UL98 standard did mention overload and endurance test but it's for make/break type of test where you flip the switch open/close. i sent the question to Eaton asking about inrush rating and duration rating but doesn't have any luck.
1. In my case i want to know if this switch can handle frequent motor start/stop and would the frequent inrush damage the switch? the client is concerned about switch will fail open and cause operation delays.
2. Response from Eaton is they cannot guarantee the switch would work indefinitely and recommended upsize or use a fused disconnect. i am looking for ideas or opinions on how to prove switch can withstand longer motor inrush.
3. The Eaton Technical Data 29-420 did mention 1800A interrupting duty and my understanding is interrupting duty is only rated for 3 cycles. which is about 0.05 sec. is there any way to prove switch will withstand 250A for 3 sec?
4. looking at the photo, the switch is very robust with thick metal contact pins, I am very confident to say the switch can withstand 240A, but there is not document to support that. based on UL98 overload and endurance test section:
In UL98 table 17, for a 75HP switch, the overload test at 480V is required to be 543A for 50 making/breaking cycles at 6 cycles per minute.
In UL98 table 19, 100A switch is required to have 10000 "with/without current" test cycles, if flipping switch open/close counts as 2 cycles, my interpretation would be the switch is good for operating 5k times.
thanks for all your help and comments.