hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 120V to 24V Edwards #592 transformer. I was wondering if its separately derived and does it require grounding electrode conductor, system bonding jumper or not?
See 250.20
Nope it's Art 725 ... see the transformer tech sheet ...So if my primary is 120V to ground supplied from panelboard 208/120V three phase with equipment grounding conductor and my secondary is 24 vac then
240.21(a) or 240.21(b) applies?
To provide some protection from a primary to secondary short in the control power transformer. Such a short is a bit more likely and more hazardous at higher voltages.So what's the technical reason for 250.20(A)(1)?
It says that with a 480V:24V transformer, you'd have to ground one of the 24V conductors. To get 24V ungrounded from a 480V (or 277V) supply, you'd have to use two transformers, e.g. 480V:120V (where one leg of the 120V is required to be grounded), and then 120V:24V.
Cheers, Wayne