greens
- Hornell, NY
- Electrical Engineer
In a solar expansion/rework, with an existing PV side-tap, we are faced with a PV combiner where the current is just over the 80% rule.
The customer is willing to disconnect a single existing small inverter, which would just satisfy 80% loading. However, since there are two arrays of panels on two ag buildings, with different insolation, it occurred to us that the max current actually produced by the equipment would be about 67.5%, two to four days of the year.
So I got called in, and was asked to find a way to "make this work." My inclination is to have the production analysis, and to also change the main on the PV combiner to 75%. The idea is that the derated main should not have nuisance trips, but the bus is protected by the derated main breaker.
This is at a residential / small agricultural operation, and if we upsize the PV combiner, we would have to upgrade the service feed, involving a long trenching job, a new combiner box, and the utility is balking at upsizing the transformer.