Arc fault breakers
Damianb86
Florida
Hi everyone. Im changing panel and all devices and and couple of lights/receptacle circuits has shared neutral. I have to install arc faults. What would be the best solution? (This is remodeled job/already finished). Thank you
Who says you need to add arc fault (AFCI)? If you didn't add any new circuits, or extend any circuits more than 6', then AFCI isn't required on just a panel change.
What is your breaker type? Some make double pole AFCIs, but they seem to be disappearing. Depending on what these serve, you could double up the hots and convert it to a single pole circuit. But you may need to run some new single pole circuits to provide adequate power or code compliant outlets (e.g. if a multiwire branch circuit provides the two kitchen small appliance circuits, you would have to split it somewhere and refeed half with a new circuit if you condensed the multiwire to single pole).
Was not required the last one I quoted a few years ago. Asked the inspector beforehand just to be sure.