basement ceiling

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
Basement in home non living space receptical in celling 7'6" off floor gfci or not ????????????????????????????????????????????????????????????????????
 
There is no height limit for GFCI protection in an unfinished basement.
 
There is no height limit for GFCI protection in an unfinished basement.
But readily accessible at that elevation becomes an issue if using a GFCI receptacle. As per article 100 definition, use of ladder is not readily accessible.
 
But readily accessible at that elevation becomes an issue if using a GFCI receptacle. As per article 100 definition, use of ladder is not readily accessible.
True and that is a separate issue. GFCI protection is required regardless of height.
 
But readily accessible at that elevation becomes an issue if using a GFCI receptacle. As per article 100 definition, use of ladder is not readily accessible.
I don't need a ladder to reach a 7'6" ceiling to hit a reset button. I don't have to able to do it with my nose. :)
 