Looking for opinions on an arc flash incident in a 3 phase LV 690V substation.
MV/LV Transformer energised. Main incomer in substation is open. Control circuitry fed from live side via a set of 690V fuses connected to live side busbar.
Voltage meter fed from live side was measuring voltages of up to 750V.
As a part of the investigation into spurious voltage readings the control fuses were subsequently pulled and replaced a couole of times and while this was being done there was a flash over and a bang.
As the voltages were reading 750V and the fuses were only rated for 690V is there a chance that the removing/replacing of these fuses while under load could have caused arcing which led to arc flash? Or any other guesses as to what coukd have caused the flash.