Alwayslearningelec
 - NJ
 - Estimator
Do you guys use feed through method( connecting right to terminals) or pigtail/splice the conductors to the terminals? Thanks
			I've been looking for 15 amp devices with pressure plate terminals.Those conductors are almost always pigtailed, via solid, to devices that have only screws.
Most premium-grade receptacles, such as Leviton Preferred, have a clamping feature.I've been looking for 15 amp devices with pressure plate terminals.
2 slots per screw for existing #12 wire is really nice when no room in box for wirenuts. The pressure plates also work for stranded, if you hate to twist & wrap around screws.
Depends, with a self grounding receptacle you only need to land 2 wires on the device which makes it easier to push it into the box especially with #10 wire.Why do most of you guys pigtail(besides qty wires in box)? isn't it easier and quicker to terminate at the device terminals?
Thanks. So what do you do with the ground wire if you have a ground wire e.g. MC cable? Also, why would you ever use #10 for standard 20A receptacles?Depends, with a self grounding receptacle you only need to land 2 wires on the device which makes it easier to push it into the box especially with #10 wire.
That is where I would pigtail.Thanks. So what do you do with the ground wire if you have a ground wire e.g. MC cable? Also, why would you ever use #10 for standard 20A receptacles?