Hello all. Please forgive what may at first glance sound like DIY questions - they are not. I've become accustomed to looking before I leap, even when I'm hiring job outs. In this case I'm project managing contractors working on a sons garage update. I don't want to piss off my service guys, yet what I read and what I'm being told don't align. Hopeful mods will consider the safety aspect of this and not think I'm trying to DIY.
I’m going to have an electrician install a sub-panel in an attached garage for electric vehicle charging. But I'm in a small town and there is still a lot of "that's the way we do it" going on. As an example, I've had several electricians tell me they use #2 aluminum for 100 amp sub-panels. They don't seem to hear "EV charging", or consider ambient temperature correction and etc.. Mind you I'm prolly the one that's wrong, but that's why I'm here - Making sure I know what a safe and professional proposal needs to include.
All said and done I want to be able to deliver 96 amps at 240 volts for more than 3 hours of constant use. This seems to mean I require wire and connectors rated to 120 amps (125%). I also need to deliver 2 amps at 120v intermittently. I assume that’s as simple as saying I need wiring for 122 amps, with a feed breaker in the main panel of 100 amps. Correct so far?
It seems easy enough until I get to wire selection vs. ambient temps. The wire will go through a garage ceiling and ascend/descend insulated walls. Here in Illinois I suppose I should assume ambient temperatures could occasionally exceed 105f in the ceilings, but it’s not likely to break 113f.
Questions:
Since I'm invariably wrong, here are the sites I've been using for reference.:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
Ambient Temperature Correction
Finally, how hard would you push on this? Again, I don't want to piss my local providers off, there aren't lots, so it's helpful to know if I'm being picky or if these are things I need to politely and gently request I be humored on.
Guys, my sincere thanks to anybody that takes the time to help me keep this thing safe!
-d
I’m going to have an electrician install a sub-panel in an attached garage for electric vehicle charging. But I'm in a small town and there is still a lot of "that's the way we do it" going on. As an example, I've had several electricians tell me they use #2 aluminum for 100 amp sub-panels. They don't seem to hear "EV charging", or consider ambient temperature correction and etc.. Mind you I'm prolly the one that's wrong, but that's why I'm here - Making sure I know what a safe and professional proposal needs to include.
All said and done I want to be able to deliver 96 amps at 240 volts for more than 3 hours of constant use. This seems to mean I require wire and connectors rated to 120 amps (125%). I also need to deliver 2 amps at 120v intermittently. I assume that’s as simple as saying I need wiring for 122 amps, with a feed breaker in the main panel of 100 amps. Correct so far?
It seems easy enough until I get to wire selection vs. ambient temps. The wire will go through a garage ceiling and ascend/descend insulated walls. Here in Illinois I suppose I should assume ambient temperatures could occasionally exceed 105f in the ceilings, but it’s not likely to break 113f.
Questions:
- Since it will be installed in an insulated wall and ceiling, am I required to request wire ampacity rated to only 60C and then derate it by .71? I seem to have read I can use 3/0 aluminum rated to 75C and derate by .82 since I’m well over 10 AWG wire. Is this correct?
- Do I have any other choices regarding acceptable temperature in insulated walls? 2/0 aluminum rated to 90c, if safe in walls and the ceiling, would also work and likely be less expensive and available. Is this allowed and safe?
- Is there any rounding allowed here? I see 1/0 90c rated wire is rated at 135 amps. Temperature corrected that’s 117.45, and the 20% constant load de-rating puts me at 93.96. Awful darn close. If it was safe.
- Regarding the whole “de-rating” thing, be it ambient temperature or extended operation, is the correct move here to simply install a 100amp 240v breaker in the main panel and fuse the sub-panel per it’s individual loads (de-rating again for the EV plugs)
Since I'm invariably wrong, here are the sites I've been using for reference.:
https://lugsdirect.com/WireCurrentAmpacitiesNEC-Table-301-16.htm
Ambient Temperature Correction
Finally, how hard would you push on this? Again, I don't want to piss my local providers off, there aren't lots, so it's helpful to know if I'm being picky or if these are things I need to politely and gently request I be humored on.
Guys, my sincere thanks to anybody that takes the time to help me keep this thing safe!