hi everyone,

Can I use wall switch to operate on/off for exhaust blower fan?

The exhaust blower is 208V, 20A, 3PH.
 
Even though the blower had means of disconnect. Is it still good to use wall switch to control motor starter?
The wall switch will be a remote control for the starter. You need to determine if there is a power outage should the fan turn on when power is restored. If you don’t want the fan to automatically restart, then you will need to use a start stop push button, so when power drops out, start button is pushed to restart.
if you use a single pole wall switch, I would use a lighted switch, light on, fan on
 
Last edited:
The wall switch will be a remote control for the starter. You need to determine if there is a power outage should the fan turn on when power is restored. If you don’t want the fan to automatically restart, then you will need to use a start stop push button, so when power drops out, start button is pushed to restart.
if you use a single pole wall switch, I would use a lighted switch, light on, fan on
I want the fan to be on when/if power is restored I case of outage so I want to use switch. Question is the fan is 3 phase, how is single pole work? Isn’t it supposed to be 3 Pole wall switch
 
I want the fan to be on when/if power is restored I case of outage so I want to use switch. Question is the fan is 3 phase, how is single pole work? Isn’t it supposed to be 3 Pole wall switch
Here's a 3 pole switch meant for motors. A few bucks more than a light switch but not much.


083348d539cd4121f9d191ec49fdab19.jpg


Sent from my SM-G965U using Tapatalk
 
The switch will work, but you will need to provide overload protection for the motor and a disconnect within sight of the motor. If the switch is considered the controller you will need a disconnect for it.
suggest you review section 430.102
 
The switch will work, but you will need to provide overload protection for the motor and a disconnect within sight of the motor. If the switch is considered the controller you will need a disconnect for it.
suggest you review section 430.102
Basically what I have from my understanding 430.102.
Panel board (208v, 20A, 3PH) breaker ——> toggle switch—-> disconnecting Means ——> exhaust fan motor

the disconnect means and motor are in sight.

article is tricky somehow it is also telling me I need disconnect switch for the controller(toggle switch)
 
Here's a 3 pole switch meant for motors. A few bucks more than a light switch but not much.

No, you can't use that.

3 phase motors have no overload protection so you have to provide a motor starter that will provide overload protection. The starter has a contactor that you can control with a single pole toggle switch to turn the fan on and off. You will also need to supply a disconnect switch in most instances between the panel and starter.

-Hal
 
No, you can't use that.

3 phase motors have no overload protection so you have to provide a motor starter that will provide overload protection. The starter has a contactor that you can control with a single pole toggle switch to turn the fan on and off. You will also need to supply a disconnect switch in most instances between the panel and starter.

-Hal
I think there are some small 3 phase motors that have built in overload protection.
 
What I am thinking is the disconnect switch, and motor starter(controller) is within sight of the motor.

And the toggle switch will not be within sight.
 
What I am thinking is the disconnect switch, and motor starter(controller) is within sight of the motor.

And the toggle switch will not be within sight.

That's usually the way it is. The toggle switch is just used to turn the fan on and off and usually located in the area it serves. It's not a safety disconnect. The toggle is just a simple single pole switch wired with a couple of #12s back to the controller. Makes it easy, rather than running all three phases back and forth.

Is this a kitchen exhaust fan?

Would this change if the motor was single phase?

If the motor has an internal overload no starter is required. You would still need a disconnect within sight of the motor.