I have a 3 yr old direct drive washer that is causing lights on the phase to pulse when agitating. The Washer is on it’s own dedicated 20a circuit that’s 25 ft away from the main service. I have placed the washer on a gfci circuit in the kitchen that’s on the other phase and it has the same effect on the lights on different circuits, but same phase.
I swapped out leds for incadesents and the pulse was still observed.
At the service panel I observed zero current on any of the circuits EGCs. The currents on the neutrals match the currents on there respective hots. Voltage from neutral to ground is zero or a few millivolts depending on what meter I use.
The amperage of the washer while on agigtation varies depending on what meter I use.
Extech showed spikes of 9amps
Fluke on min max showed as high as 13.7a
Fluke 43b showed 19a. Using sags and swells.
Washer outlet min voltage- 123.5
Washer outlet max voltage - 124.7
Service panel voltage same phase as washer-123.8 min 124.7 max
Min max at washer outlet 124.7 max 123.1 min 124.3 avg using fluke1587
Light circuit voltage matches panel voltage.
Logic tells me I should be seeing a bigger voltage drop but I’m not.
I measured my dryer since it’s 240v load with neutral.
Non load voltage 125.6 max 125.2 min
Non washer phase on start up showed max 125.5 min 121.7 with current up to 38a settling at 25a 124.4 max and 124.0 min
washer phase on start up 126.9 v max 1241. Min amperage 4.32a settling at 23a with 124.6 max 123.8 min
I have plugged in a 10.5a vacuum on washer outlet and observed a 1.5v change at the outlet. I observed a volt change on the same phase at the panel. The other phase increased by. 3v.
I don’t see anything nefarious. Can I assume the washer is causing the issue?