The electrical Engineer shows in the plans 2-16.0KW heaters and 1- 6.0KW CV boxes.. The CV boxes are located in different Rooms. The 480 3 PH. 20A breaker would trip when more then 1 heater was on-line. He stated that the E.C. made a mistake and the breaker in that slot was supposed to be a 30 Amp. Breakers were changed and called it ok. The AWG is 12 THWN, about 50ft from source. Since each serves a different room and a thermostat per unit noncoincident loads would not apply. I may be wrong, but if I do not ask, I do not learn.. Thank You