Can I land GEC in isolated ground bar
TimWA
Dear Users,
Can I land my #6 solid GEC in an isolated bonded ground bar in the first-disconnect panel (image attached)? Or must it land in the bonded grounding (neutral) bus only? Not finding specific GEC stipulation either way.
If the neutral bus only, could I still leave the GEC where it is and install #4 bonding jumper between the two busses?
It should reach the neutral bar on the left. The GEC can carry some current and you wouldn't want that through the can that the equipment ground bar is bonded to. Then it may be best to run another #6 from the ground rod with an additional acorn. If the other ground rod is on the other side of the h frame it might not be that har to come from that one to the other panel.
Sent from my SM-S367VL using Tapatalk
But the I believe the OP has the option to remove the MBJ screw and install a wire-type MBJ from the neutral bus to the grounding bus, and then 250.24(A)(4) allows the GEC to connect to the grounding bus rather than the neutral bus.
Cheers, Wayne
Cheers, Wayne
That is correct. If the MBJ is a wire or busbar then the GEC can connect to the EGC bus. You would remove the green screw. {250.24(A)(4)}