ndan305
- Seattle, WA
- Engineer
Does the continuous load factor of 125% apply to motor loads and AC equipment?
For example:
I have a panel with:
1x AC unit, using MCA and MOP on nameplate
1x 2 hp motor, using 1.25*FLC
1x combination motor (2 hp and 1 hp motor), using 1.25*FLC largest motor + FLC smaller motor
The three loads are continuous loads that can operate more than 3 hours. Do I add up all the loads and add 25% on top of it to size my feeder conductors and panel breaker?
Then going on to service loads feeding the panel.. add another 25% on top of what we added up so far? It seems like safety factor on top of safety factor.
Panel load = total continuous load*1.25
Service load = panel load*1.25
For example: