mathan1987
- Seattle
- Electrical design engineer
What are the factors to consider when choosing the voltage of the power distribution system 208V/ 480V?
As often as not the choice is made for you by the utility. They have rules about such things.What are the factors to consider when choosing the voltage of the power distribution system 208V/ 480V?
We have a double-ended feed here. One is from the utility and the other is a redundant backup from on-site generation. They are medium voltage.The plant I was responsible for was supplied by medium voltage from the utility so we were free to choose our secondary voltage(s). Perhaps that is the situation for the OP?
Our shop utilized 480/277. 480 for machine tools, 277 for lighting.
208/120 supplied the office. 208 for HVAC and data center, 120 for office lighting and general purpose.
There is a limit as to the economic feasibility of operating at a certain voltage. For the same amount of power transferred on a circuit, large current is handled if low voltage systems are chosen than if they are operated at higher voltages. That said, use lower voltages for safety or choose higher voltage to clip on costs of electrical distribution materials (high currents requires larger wires).