Service panel is a sub panel

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
A customer's house service panel is wired as if a sub panel, ie., ground bar is not connected to neutral. Neutral bar is floating. No outside disconnect. No ground rod. Probably the 1956 home was a DIY fuse panel replacement?.... We told the owner, but they are thinking about having us correct it. How dangerous is this ? I did have my worker install a jumper between the ground and neutral bars.
 
Is the panel fed with metal raceway? If not then there is no ground protection at all. The egc's are basically worthless.
 
A customer's house service panel is wired as if a sub panel, ie., ground bar is not connected to neutral. Neutral bar is floating. No outside disconnect. No ground rod. Probably the 1956 home was a DIY fuse panel replacement?.... We told the owner, but they are thinking about having us correct it. How dangerous is this ? I did have my worker install a jumper between the ground and neutral bars.
so what do you think the big problem is as long as the EGC and N are bonded at the panel?
 
No ground rod, but is there a bond to a water pipe? If the house has city water, the water pipe will do more than one or even two ground rods.
 