Theclash84
- Missouri
- Estimator
At the breaker, downstairs. The shorted wires were upstairs.Where was the arc, at the short or at the breaker?
I would definitely replace the breaker, then.At the breaker, downstairs. The shorted wires were upstairs.
It was a brand new Square D breaker.
HOMHOM or QO?
Really depends on how much fault current flows and time til opening the circuit.I don't know what brand of breaker you were useing but it doesn't sound like it was in good condition to start with.
Normally with a 20 amp breaker you won't hear any boom and no big arc flash even when it's a short. Normally the breaker will just click off.
What brand of breakers are you dealing with? Federal Pacific may get you a good boom (can be hard to trip) but they cost more than even an expensive imported beer ( purchased at the airport).
I tried to upload a pic, but the file size is too large for the forum to upload...tried a few different things to compress the file, but was unable. At any rate, there is no visual damage to the exterior of the breaker or the breaker contacts. Also no visible damage to the bus bar on the service panel.Since you are going to replace the breaker anyway. Rather than throwing it away. I would be interested in what the insides look like. That may give you some idea how long the breaker "would have" lasted. Whenever I do stupid things, I like to learn from that experience. This way I could learn without having to go through the experience of an arc flash.
OK, but what does the breaker look like inside? An arc flash like that at the breaker is very likely to have damaged something, it seems to me.I tried to upload a pic, but the file size is too large for the forum to upload...tried a few different things to compress the file, but was unable. At any rate, there is no visual damage to the exterior of the breaker or the breaker contacts. Also no visible damage to the bus bar on the service panel.
Roughly 10' of romex from the breaker to a junction box where it branched out. The shorted wires ran another 10' from the junction box to a switch box in the wall, so 20' total.If there is no visible arc extinguishing product, like soot, visible on the exterior of the breaker, I would not be surprised to find your fault was on a medium level event. Most of us have never seen a breaker as it interrupts faults above a few thousand amps.
How long were the conductors between the breaker and the fault point? #12 AWG is pretty good at limiting fault current.
I test power circuits with FETs and IGBTs to failure in the course of design/development.It was a brand new Square D breaker.
Unusual for a QO to go boom, so if a Homeline has the same guts, should be the same. I’ve had QO and CH breakers that trip without as much as a whimper on a short, but GE and BR you know it! LOL!HOM breakers have the same internal trip mechanism as their QO equivalents.
I kind of wonder if this wasn't some sort of knock-off or counterfeit version of a Square D breaker. Those things do have a way of getting into the supply chain.Unusual for a QO to go boom, so if a Homeline has the same guts, should be the same. I’ve had QO and CH breakers that trip without as much as a whimper on a short, but GE and BR you know it! LOL!
Yep. Definitely a bit crispy around the edges.Amazing, from outside no appearance of a problem but inside wow, never would have suspected that much burn.
I guess I've always expected the QO line to be superior internally in addition to externally. I've never researched it, but I might now. Other than trip indication and 3 pole options, I figured there would be something better about them.Unusual for a QO to go boom, so if a Homeline has the same guts, should be the same.
Nope. 40 years ago they were designed to use common components, the differentiator was the trip indicator and the plug on jaw.Holy crap? That was from one short circuit event? I wouldn't have expected that.