jharlow22
New User
- Location
- Melbourne, FL
- Occupation
- Contractor
Just failed an inspection during a remodel. We picked up a 12/2 20 amp homerun and branched off for new outlets (15 amp) for rough in with 14/2. Never been a problem before.
The failure was correct. The wire size must be maintained for the entire circuit, regardless of expected load.Just failed an inspection during a remodel.
I would say the inspector didn't actually look at the whole circuit.Just failed an inspection during a remodel. We picked up a 12/2 20 amp homerun and branched off for new outlets (15 amp) for rough in with 14/2. Never been a problem before.
At one time long ago, it was allowed for switch legs only. You can change the breaker to 15 amps though, and be back legal. (Unless it feeds an area that requires 20 amp). Inspector was on his game, and correct.Just failed an inspection during a remodel. We picked up a 12/2 20 amp homerun and branched off for new outlets (15 amp) for rough in with 14/2. Never been a problem before.
Actually it doesn’t, it just needs to have the ampacity above the rating of the ocp.Welcome to the forum.
The failure was correct. The wire size must be maintained for the entire circuit, regardless of expected load.
While a common practice in some areas, I don't think that the NEC ever permitted 14 AWG switch loops on a 20 amp circuit.At one time long ago, it was allowed for switch legs only. You can change the breaker to 15 amps though, and be back legal. (Unless it feeds an area that requires 20 amp). Inspector was on his game, and correct.
Actually it doesn’t, it just needs to have the ampacity equal to or above the rating of the ocp.
Right. I meant for the 20a circuit in question.Actually it doesn’t, it just needs to have the ampacity above the rating of the ocp.
For some reason it sticks in my mind when I was at trade school. Maybe 78’ nec edition? I never liked it, and never did it, but seems like later I heard it was changed due to remodels where they changed the switches to receptacles?While a common practice in some areas, I don't think that the NEC ever permitted 14 AWG switch loops on a 20 amp circuit.
if the 14 was on a ocpd would it be a tap?For some reason it sticks in my mind when I was at trade school. Maybe 78’ nec edition? I never liked it, and never did it, but seems like later I heard it was changed due to remodels where they changed the switches to receptacles?
Like Don, I constantly saw it done, but never saw it legal in codebook (started in late 70's)For some reason it sticks in my mind when I was at trade school. Maybe 78’ nec edition? I never liked it, and never did it, but seems like later I heard it was changed due to remodels where they changed the switches to receptacles?
That is not true, as long as all the conductor sizes are protected by the OCPD.Welcome to the forum.
The failure was correct. The wire size must be maintained for the entire circuit, regardless of expected load.
Right. Addressed in post #10.That is not true, as long as all the conductor sizes are protected by the OCPD.