Here's the setup & issue.
208v3ph60Hz service, fused disco is the main, then dumps into a breaker panel.
Service (disco) is fused 100A. (currently assumed ~35kva / 100A service)
Shop installed 208v3ph 77A rated equip (motors).
The breaker panel has 100A 3ph to the equip.
The std "fast" fuses in disco pop (usually one) during equip start.
Can the disco fuses be replaced with slow-delay type if the breaker panel has equip and other branch ckt's on it?
I would recommend an upgrade to 200A service, but shop guy does not want to go there just yet, hence the ask about changing fuse type.
208v3ph60Hz service, fused disco is the main, then dumps into a breaker panel.
Service (disco) is fused 100A. (currently assumed ~35kva / 100A service)
Shop installed 208v3ph 77A rated equip (motors).
The breaker panel has 100A 3ph to the equip.
The std "fast" fuses in disco pop (usually one) during equip start.
Can the disco fuses be replaced with slow-delay type if the breaker panel has equip and other branch ckt's on it?
I would recommend an upgrade to 200A service, but shop guy does not want to go there just yet, hence the ask about changing fuse type.