two electric sources in one building

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
Does NEC allow two sources (from two separate meters) to enter a building ? Customer has a detached building (barn) fed from the meter on the house , 30 amps. But they want to add a 50 amp RV, so, we may add another meter/service on the barn. They would like to use both means of power. Is that allowable ?
 
IMO, there is no definitive answer in the nec. The nec states that a build can only be fed with one feeder or one service but you have a service and a feeder. One can argue that the feeder or branch circuit from the house is from a different service which would not allow the install.
 
Why not use a RV meter pedestal? That way, it’s independent of the barn? Or if the RV is “stored” in the barn (most likely somebody is living in it) install a new 100 amp service on the barn, remove the 30 amp feeder.
 
Do they want to pay the monthly meter fee on that 2nd meter for the rest of their life? I think my meter fee is $10/month whether I use any power or not. That could make sense if they are renting out the RV spot. What would it cost to replace the feeder with something larger?
 
Thank you all. To replace the barn feeder with a larger capacity underground from the house would take $4700. And I would rather leave the existing 30 amp feed intact because then I wouldn't have to re run wiring to the first and second story lighting and outlets and outside lighting, etc when I install the new 100 amp panel,
 
Does NEC allow two sources (from two separate meters) to enter a building ? Customer has a detached building (barn) fed from the meter on the house , 30 amps. But they want to add a 50 amp RV, so, we may add another meter/service on the barn. They would like to use both means of power. Is that allowable ?
Thank you all. To replace the barn feeder with a larger capacity underground from the house would take $4700. And I would rather leave the existing 30 amp feed intact because then I wouldn't have to re run wiring to the first and second story lighting and outlets and outside lighting, etc when I install the new 100 amp panel,
But I thought you were looking at adding a separate meter for the RV? Is the existing 30 amp feed at a point on the barn that cannot be intercepted, and fed from the new service? Why would the barn require rewiring?
 
Does NEC allow two sources (from two separate meters) to enter a building ? Customer has a detached building (barn) fed from the meter on the house , 30 amps. But they want to add a 50 amp RV, so, we may add another meter/service on the barn. They would like to use both means of power. Is that allowable ?
In my area they allow a single & a 3 phase service. At the large 550 bed hospital that I retired from they had a large expansion with 10 floors. They added another 13,000 dual service so they had 4 separate services. There was no room in original switchgear room or even 2 basement floors to add the new service so while it was located in same building were at least 700' apart. They usually insist that they services disconnects be in the same area.
 