First thing is first i want to Thank all of you for any and all help! This forum is very much appreciated!!! I have never done a PLC install. The company I'm working for is changing there existing system to a plc by Kahler Automation system. There is no engineering involved so i am design this my self... the existing plant is a cobbled together mess... I see in my field wiring diagram that i have around 165 16 gauge 24voltdc conductors that go from my plc to various locations on site such as hmi, remote start/pause, emergency stops, Air solenoid valves ect. as i understand these should be considered class 2 circuits. I plan on using 16 guage thhn/thwn. I was trying to figure out my pipe fill calculations for my raceways, but was not having any luck finding anything smaller than 14guage wire.... I didnt know if there was a better solution or a type of cable that i could use.... I have a Beldan 28330a which is a 16 conductor of 16guage wires i didnt know if that was more of standard or what should be used. I planned on using pvc raceways since its a corrosive environment and i only have about 36 days to get the job complete... I will try and post some pictures to represent the specific scope of work .....