Good Morning:
I was wondering if someone could help me understand the following question Thank you:
Insulation resistance tests are best made with a direct-reading Megger. These tests can
also be made with a high-resistance voltmeter and a source of d.c. supply. Assume that a direct reading instrument is not available but you have on hand a 100-volt voltmeter having a sensitivity of 5000 ohms per volt and a 100-volt battery. The battery is connected in series with the voltmeter. One free battery lead is connected to the wire whose insulation resistance is to be measured, and the other free lead to the grounded circuit. With this hookup, the volt meter
reads 50 volts.
22. The insulation resistance, in ohms, of the above conductor is
A. 500 B. 5,000
C. 250,000
D. 500,000
23. The resistance, in ohms, of the above-mentioned voltmeter is
A. 500 B. 5,000
C. 250,000
D. 500,000
reads 50 volts.
A. 500 B. 5,000
C. 250,000
D. 500,000
A. 500 B. 5,000
C. 250,000
D. 500,000