jaggedben
- Northern California
- Solar and Energy Storage Installer
I don't think that the 2020 language actually changes anything here.
			I agree with you that the above should be true. However, you have to allow for the fact that the NEC is illogically often written. Under your interpretation, the last sentence of 705.12(B)(3)(6) would be meaningless, as it grants permissions that you already have. And the first sentence would automatically qualify any panel with feed through lugs and conductors. Both of those conclusions are nonsensical.The first sentence of 705.12(B)(3)(6) remains standing without being qualified by the second.
The second sentence of 705.12(B)(3)(6) only servs to give more options in the specific case "Where overcurrent device is installed at the supply end of the feed-though conductors … " so not this case, then disregard.
Kirchoff's current laws are at the base of the NEC rules and should be considered when interpreting the code.I agree with you that the above should be true. However, you have to allow for the fact that the NEC is illogically often written. Under your interpretation, the last sentence of 705.12(B)(3)(6) would be meaningless, as it grants permissions that you already have. And the first sentence would automatically qualify any panel with feed through lugs and conductors. Both of those conclusions are nonsensical.
So instead, 705.12(B)(3)(6) must be read as intending to mean "Connections shall be permitted on busbars of panelboards that supply lugs connected to feed-through conductors (only if you comply with the rest of the section.) The feed-through conductors shall be sized in accordance with 705.12(B)(1). Where an overcurrent device is installed at the supply end of the feed-through conductors, the busbar in the supplying panel board shall be permitted to be sized in accordance with 705.12(B)(3)(1) through 705.12(B)(3)(3) (otherwise, it is not permitted, and you can't comply with 705.12(B)(3))."
BTW, seems like 705.12(B)(3)(6) is a step backwards as far as 705.12(B)(3)(1) goes. I don't see any issue that feed through lugs cause when a panel complies with 705.12(B)(3)(1). So there should be not further restrictions or requirements for OCPD on the feed through conductors to qualify the busbar via 705.12(B)(3)(1).
Cheers, Wayne
My attempt at that is the blue arrows in the diagram in post #28Kirchoff's current laws are at the base of the NEC rules and should be considered when interpreting the code.
Agreed in principle (mostly for interpreting the ambiguous), but what conclusion you draw from that which bears on my quoted post escapes me.Kirchoff's current laws are at the base of the NEC rules and should be considered when interpreting the code.
Sorry; I should have just entered a post instead of replying to yours. Apologies.Agreed in principle (mostly for interpreting the ambiguous), but what conclusion you draw from that which bears on my quoted post escapes me.
Cheers, Wayne
I don't think its on us as electricians to read into what the NEC intends, if 705 is so bad we have to read into what it intends, thats a legally ambitious territory.So instead, 705.12(B)(3)(6) must be read as intending to mean
Not to get too philosophical, but you always have to read intention into the words in any book. That's the nature of language.I don't think its on us as electricians to read into what the NEC intends, if 705 is so bad we have to read into what it intends, thats a legally ambitious territory.
What the OP is proposing no inspector can refute and if he appealed an AHJ he would prevail in court.
Not in a court room, show that sentence to a lawyer, It not enforceable.you always have to read intention into the words in any book. That's the nature of language.
That would depend on what "supply" means. If "supply" means grid, I don't see how you can defend that interpretation. But if the PV were interconnected in the subpanel, you could argue that "supply" actually means the alternate source (PV) in that sentence, and so the subpanel main breaker would be at the supply end of the feed-thru conductors.My philosophical argument is the main breaker in the last panel is still at the supply end of the feed thru conductors.
And courts consider the intention of the law all the time.Not in a court room, show that sentence to a lawyer, It not enforceable.
I am not a PV guy here, but code is a law all the OP needs to do is comply with the law.
The way you described the existing installation it's clearly at the load end. So I don't get how you can say this.My my philosophical argument is the main breaker in the last panel is still at the supply end of the feed thru conductors.
usually only when there is ambiguity.And courts consider the intention of the law all the time.