jaggedben
- Northern California
- Solar and Energy Storage Installer
Which is the case most of the time when you're talking about the NEC.usually only when there is ambiguity.
Yes, read literally the first sentence says that to comply with (2020) 705.12(B)(3), all you need to do is add some feed-thru lugs and feed-thru conductors, and then you can load up the bus all you like. But everyone knows that is not what is meant and would not be safe. The CMPs need to learn how to write logically.OK I just looked up 705.12(B)(3)(6) while I am waiting in my truck, this is not vague at all first sentence is declarative and not conditional on anything following. "shall be permitted" is the only qualifier in that first sentence.
Incorrect it says 705.12(B)(1)Yes, read literally the first sentence says that to comply with (2020) 705.12(B)(3)
Incorrect 705.12(B)(1) (a) or (b) would not permit that.all you need to do is add some feed-thru lugs and feed-thru conductors, and then you can load up the bus all you like.
My statement was correct. The unreasonable literal reading goes like this:Incorrect
Please provide some examples of how one could "load up the bus all you like" and comply with 705.12(B)(1)?Yes, read literally the first sentence says that to comply with (2020) 705.12(B)(3), all you need to do is add some feed-thru lugs and feed-thru conductors, and then you can load up the bus all you like.
OK, 200A service, meter/main/distribution with 200A main breaker and feed-thru lugs, 200A feed-thru conductors to a 200A main breaker subpanel. Now let's put another 400A of load breakers on the service panel bus, and 200A of PV breakers. The feed-thru conductors still comply with 705.12(B)(1)(b) because of the main breaker on the subpanel.Please provide some examples of how one could "load up the bus all you like" and comply with 705.12(B)(1)?
Nope that's a violation of 705.12(B)(1)(b)OK, 200A service, meter/main/distribution with 200A main breaker and feed-thru lugs, 200A feed-thru conductors to a 200A main breaker subpanel. Now let's put another 400A of load breakers on the service panel bus, and 200A of PV breakers. The feed-thru conductors still comply with 705.12(B)(1)(b) because of the main breaker on the subpanel.
Cheers, Wayne
Care to expand on that? I don't see it.Nope that's a violation of 705.12(B)(1)(b)
We agreeAh, I was wondering if you were thinking about applying 705.12(B)(1) to busbars. To answer your first question, yes, busbars are feeders per the definition,
the usage of the word feeder in the NEC often, and in 705.12(B)(1) in particular, excludes busbars in panelboards.
Agreed[If there is only one load breaker between the two source connections (the busbar has just 3 connections), then 705.12(B)(1)(b) could be used, and so there's no problem.
Agreed, that would make it clear.In fact, the 705.12(B) would be improved if 705.12(B)(3) were limited to busbars with 4 or more connections, and busbars with only 3 connections were subject to 705.12(B)(1) instead.
I agree that is a plausible logical way to read 705.12(B)(3)(6) based on the definitions. However, I'm confident that is not what was intended, and that in 705.12(B), "feeder" is used to mean a non-busbar feeder, and that "feed through conductors" is meant to exclude the busbar.In this special case of 706.12(B)(3)(6) the busbar in the supplying panelboard together with the feeder wires to the second panel are all conductors of one feeder that "feeds-though", only then can one use 705.12(B)(1).
The intent is for 705.12(B)(3)(6) to treat the busbars and the attached feeders as one and have them be sized(f) Connections shall be permitted on busbars that supply feed-through lugs and conductors
connected to the lugs opposite the main source of supply. The ampacity of the busbar and connected
feeders shall not be less than the sum of the primary source overcurrent device and 125 percent of the
power-source output circuit current.
Connections shall be permitted on busbars of panelboards that supplyfeed-throughlugsandconnected to
conductorsthe lugs opposite the main source of supply.feed-through conductors. The
feed-through conductors shall be sized in accordance with 705.12(B)(1) . Where an overcurrent
device is installed at the supply end of the feed-through conductors, the busbar in the supplying
panelboard shall be permitted to be sized in accordance with 705.12(B)(3) (1) through 705.12(B)
(3) (3).The ampacity of the busbar and connected feeders shall not be less than the sum of the
primary source overcurrent device and 125 percent of the power-source output circuit current.
All they say in the Resolution Statements regarding705.12(B)(3)(6) isRejected but see related SR
705.12(B)(3)(6) is further edited to clarify how panelboards with feed-through conductors shall be
sized and how the feed-through conductors are sized.
The main breaker in the supplying panel protects the feed-thru, a MLO would not.I would say the diagram does not comply with 2020 NEC 705.12(B)(3)(6). That requires "an overcurrent device . . . installed at the supply end of the feed-through conductors," to allow the use of 705.12(B)(3)(3) for the panel busbar.
Sorry if this was combat by text, I hope you mean you find my arguments convincing. Totally agree that these sections were not written by anyone with adequate logical training.Wayne I am surrendering to all your interpretations so far other than this one:
I can buy that if there are no secondary sources attached to breakers on the bus. In which case the secondary source (the only reason to be looking at 705.12) would be attached via the feed-thru lugs, i.e. in the panel supplied by the feed-through conductors, or a feeder interconneciton to the feed-through conductors. If there's a secondary source on a breaker on the panelboard bus, then there's no one breaker protecting the feed-through conductors, and since 705.12(B)(3)(6) uses the singular, I would say that doesn't comply.The main breaker in the supplying panel protects the feed-thru, a MLO would not.