On a project where there is a heat trace panel fed temporarily from a genset at 208/120v. They thought it was 277v checked generator and verified it has been powering the 480/277v panel with 208/120v.
We just installed purchase power today and will be re-feeding the panel with the correct voltage (480/277v). All the heat trace circuits are single phase 277v (line-neutral loads)
As of now with the 3ph 4w 208/120v I have around 50amps per phase. This is self regulating heat trace. 10watts per foot at 240volts (manufacture says it’s good from 208-277v)
We have to re-size the feeder and raceway feeing the panel.
My big question that I cannot make sense of today (struggling with a sinus infection my excuse lol) When we change the system voltage from 208/120v to 480/277v the current should increase because of all the loads being strictly resistive right?
Again all loads are single phase (line to neutral) so right now it is 120v but will be changing to 277v line to neutral.
But since it’s from a 3ph 4w system is this math correct.
(208v x sqrt3 )x 50amperes= 18kw
18kw/ (480v x sqrt3)= 21.6amperes.
We just installed purchase power today and will be re-feeding the panel with the correct voltage (480/277v). All the heat trace circuits are single phase 277v (line-neutral loads)
As of now with the 3ph 4w 208/120v I have around 50amps per phase. This is self regulating heat trace. 10watts per foot at 240volts (manufacture says it’s good from 208-277v)
We have to re-size the feeder and raceway feeing the panel.
My big question that I cannot make sense of today (struggling with a sinus infection my excuse lol) When we change the system voltage from 208/120v to 480/277v the current should increase because of all the loads being strictly resistive right?
Again all loads are single phase (line to neutral) so right now it is 120v but will be changing to 277v line to neutral.
But since it’s from a 3ph 4w system is this math correct.
(208v x sqrt3 )x 50amperes= 18kw
18kw/ (480v x sqrt3)= 21.6amperes.