guschash

Senior Member
Location
Ohio
I needed to fed HO garage from his basement . It was a attach garage with breeze way between house and garage , maybe 10ft between them. there concrete walkway leading to service door. No way to get under concrete because the whole area between house and garage is concrete . So I came out from basement about 12" above ground ran along house 4ft to corner of house and breeze way ,then up and across breeze way 6' to garage then into garage. I used SE cable because coming out of basement, house corner went back 4" then over to breeze, then across breeze to garage . My question is is it alright to run cable 4" above ground for 4' before going up side of house?
 
I needed to fed HO garage from his basement . It was a attach garage with breeze way between house and garage , maybe 10ft between them. there concrete walkway leading to service door. No way to get under concrete because the whole area between house and garage is concrete . So I came out from basement about 12" above ground ran along house 4ft to corner of house and breeze way ,then up and across breeze way 6' to garage then into garage. I used SE cable because coming out of basement, house corner went back 4" then over to breeze, then across breeze to garage . My question is is it alright to run cable 4" above ground for 4' before going up side of house?
Is it subject to physical damage? If so would need to be in conduit.
 
Why not install conduit and LB's? It would look so much nicer and the physical damage worries would be not exist. Just remember, the inside of a conduit installed on the outside of a building is considered a wet location. Wire accordingly. :)
 
Yes SER cable . It's 12" above ground for 4or 5 feet. I don't see how it could get damaged , unless someone went out of his to damage it.
At 12 inches, there are many ways accidental unintentional damage can occur, Lawn mower wheel or frame, snow blowers etc. And as that cable gets older the likelyhood of damage increases because of sheathing flexibility diminishes and becomes brittle. Seen many instances where the simple act of the painter setting up a ladder making contact that wouldn't bother a new cable, now cracks open the older cable. Got one in my dumpster right now that we replaced, because of some cracking that let water into the cable, as it was being pulled down and flexed it shattered as it bent. That cable was only 20yrs old based on inspection sticker and build date.
 