Photo Voltaic isn't my expertise although I did go to a class or two, which wont help your question I'm sure .. but the only place the neutral and ground connect in my electrical world is at the point of origin of the utility neutral, anywhere down stream from that origin point they are to be isolated from one another, basically because the neutral is a current carrying conductor and one does not want to connect that potential with a ground conductor which then could inadvertently allow a conductive path onto a metallic surface which people may come in contact with.I have a PV system line side tap, with PV AC disconnect. where will my neutral and ground bond location. in my MSP or PV Disconnect? is there a difference if the location is in PV disconnect or MSP or both. Thank you
based on my research bond location is on the first disconnect. it's hard to tell which is the first disconnect
Are you considering, or is the PV ever considered a SDS? If not the N/G bonding is to be at one location only.
Both are service disconnects and need main bonding jumpers.based on my research bond location is on the first disconnect. it's hard to tell which is the first disconnect
Technically speaking, not really, because there is no EGC where meters are normally installed. The meter enclosure is part of the neutral itself.Meter sockets also force you to bond neutral and ground, which would make a redundant N-G bond from the service disconnect.
I think this is interchangeable. I was corrected by my instructor before. I took up a class and install the wire from the load side and she said it should be on the line side because the PV system is the source.Your line/load orientation is backwards on that disconnect. The line side terminals to the top of the disconnect, should be toward the utility. The line side terminals on the top of the disconnect are usually covered with a plastic shield to mitigate the risk of accidental contact. The permanently energized source belongs connected to the top terminals. This way, as much of the disconnect interior is de-energized as possible, when it is in the open position. The fuses would then be de-energized, and so would the open blades. Disconnects and fuses are inherently capable of carrying current in either direction, but voltage energization should be established on the top terminals.
It is good to draw it on your diagrams so its up/down orientation matches the way it is arranged in reality, as this is something that is easily overlooked, and could be a costly mistake requiring a new shutdown to fix. When an installer sees that you've deliberately gone out of your way to put the line side terminals on the top of your drawing, this helps comprehension. If by contrast, it looks like just a switch that is in-line with your circuit, the installer might wire it backwards and not realize that the device is meant to be wired a certain way.
Not universally; here in Texas there are only two AHJs I know of who want to see this. The rest want an EGC through the disco to the PV system and N and G unbonded in the PV AC disco. Botttom line: look at any documentation that there may be in the AHJ PV system requirements, or if there aren't any, ask them.Both are service disconnects and need main bonding jumpers.
Again, many AHJs here in Texas do not see it that way.This causes confusions with the AHJ's in NC so much that there are example drawings on the fire marshal website. Think about it like this, if you turn off the main breaker will the PV system still have power? If so you need to bond the neutral in the PV disco, as this is the first means of disconnect.
I understand they get to run their own jurisdictions but I don't quite get the logic behind that decision either. Do they require the fused AC disco to be marked as "service equipment"?Again, many AHJs here in Texas do not see it that way.
They do not require us to label the PV AC disconnect with anything other than what NEC 690 requires.I understand they get to run their own jurisdictions but I don't quite get the logic behind that decision either. Do they require the fused AC disco to be marked as "service equipment"?
So I get the 690 requirements of course but it also falls under the definition for Service Equipment which has it's own requirements for bonding and marking. I know this is a moot point I just find it curious.They do not require us to label the PV AC disconnect with anything other than what NEC 690 requires.
The AHJs that direct us to leave G and N unbonded in the PV AC disco also require us to run a grounding conductor through the disco back to the main distribution panel from the PV system, so they do not consider it to be a service.So I get the 690 requirements of course but it also falls under the definition for Service Equipment which has it's own requirements for bonding and marking. I know this is a moot point I just find it curious.