I am a little confused. We do not do many pools on new homes. In this case the pool light transformer will be on the opposite side of the home from the breaker panels and other pool equipment. We follow 2017 NEC.
My INTENT is to install a NM-B 14 AWG wire from switchbox to a junction box at the wall penetration to an outside bell box. Then conduit from bell box with THWN to a pool transformer and the same to a pool rated junction box. All conduits will be duct sealed to prevent gas transfer. I see the NM as protected from all corrosive gas.
I want to power my light from a switch connected to a 14 AWG local general purpose power source already located in the switchbox. Switchbox is located inside the home. I THINK 680.23(f)(1) allows this as no part of the NM-B will be in a corrosive environment. Paraphrased, 680.23(f) states Where installed in non-corrosive environments, you can use any chapter 3 wiring method.
Now, 680.23(f)(2) contradicts this by basically stating you must use a minimum size 12 AWG and insulated grounding conductor. This contradicts the previous statement of allowing any chapter 3 wiring method.
In my case, this would mean I have to pull a dedicated circuit about 80 feet in conduit or M/C for the 1Amp pool light and I clearly would like to avoid this.
My INTENT is to install a NM-B 14 AWG wire from switchbox to a junction box at the wall penetration to an outside bell box. Then conduit from bell box with THWN to a pool transformer and the same to a pool rated junction box. All conduits will be duct sealed to prevent gas transfer. I see the NM as protected from all corrosive gas.
I want to power my light from a switch connected to a 14 AWG local general purpose power source already located in the switchbox. Switchbox is located inside the home. I THINK 680.23(f)(1) allows this as no part of the NM-B will be in a corrosive environment. Paraphrased, 680.23(f) states Where installed in non-corrosive environments, you can use any chapter 3 wiring method.
Now, 680.23(f)(2) contradicts this by basically stating you must use a minimum size 12 AWG and insulated grounding conductor. This contradicts the previous statement of allowing any chapter 3 wiring method.
In my case, this would mean I have to pull a dedicated circuit about 80 feet in conduit or M/C for the 1Amp pool light and I clearly would like to avoid this.