jaggedben
- Northern California
- Solar and Energy Storage Installer
I think a lot of this is due to hangups about the meaning of words and ignorance of the physics and engineering. But yeah, AHJs will ask for stuff.
I get it, since you are running 4 wire they don’t want you to bond again which I do agree with. That is why it is so hit and miss in each jurisdiction we go to. IMO for a line (supply) side tap there should only be a three wire connection to the panel you are tapping and then the main PV disco should tap the existing GEC. Of course they don’t often ask for my opinion……The AHJs that direct us to leave G and N unbonded in the PV AC disco also require us to run a grounding conductor through the disco back to the main distribution panel from the PV system, so they do not consider it to be a service.
I was taught by a person I totally respect to look at a tap as if the panel the tap was in was non-existent. So by looking at it in that light there is no neutral/ground bond in the newly created service panel. Of course as stated earlier, this really only works with a three wire connection in the tapped panel. Code allows you to ground the neutral at any accessible point 250.24 which could be the original service disco as well as the new service disco. The main objective is to not have a parallel path which theoretically could allow fault current to flow in a circular motion without tripping the OCPD, theoretically.What exactly is the Physics behind having multiple N-G bonds when you have multiple service disconnects? Is this just an oversight of the code, that we end up having to follow to make a compliant install? Or is there a physical basis for this to happen?
I understand the Physics behind restricting the number of places an N-G bond occurs, to avoid letting the EGC and other electrically inactive metal be in parallel with the neutral and carry objectionable current. However, this doesn't explain the double standard about why you get to / have to install multiple N-G bonds with multiple (separately-installed) service disconnects.
You can have parallel current paths in the neutral and equipment ground in systems with a grounded conductor that can desensitize the OCPD. But that's not circulating current.The main objective is to not have a parallel path which theoretically could allow fault current to flow in a circular motion without tripping the OCPD, theoretically.
Where does it say that? Is it in so many words specific to PV or is it an interpretation based on what it says about other things? None of the AHJs we deal with here in Texas have changed what they expect to see; a couple of them want a N-G bond in the PV AC disco and all that goes with that, but the rest do not.Texas adopted the 2020 NEC in 11/2020 and the 2020 NEC requires the N-G bond in the PV disconnect.
My point about physics there is no meaningful difference to the safety of people or property between a service disconnect and a supply side PV disconnect. And since the purpose of the code is to ensure safety, I do not see, and have never seen, why the code should allow or prohibit different installation practices, regardless of what those practices might be. And yet, by accident (in my estimation), because of the way certain things are defined and described in the code, they get treated differently. (In my opinion the only disconnect that is connected directly to the service that should be treated differently than a service disconnect is the fire pump. But the code as written is a long way from that. There are literally a dozen or so sections that would have to be revised.)What exactly is the Physics behind having multiple N-G bonds when you have multiple service disconnects? Is this just an oversight of the code, that we end up having to follow to make a compliant install? Or is there a physical basis for this to happen?
See the new section 250.25Where does it say that?
250.25Where does it say that? Is it in so many words specific to PV or is it an interpretation based on what it says about other things? None of the AHJs we deal with here in Texas have changed what they expect to see; a couple of them want a N-G bond in the PV AC disco and all that goes with that, but the rest do not.
They can do that. I remember in Hawaii before they got everyone on the same train that there were some AHJs with an NEC that was five revisions old. Made PV really hard.BTW, although as a state Texas has adopted the 2020 NEC, jurisdictions within the state can opt out; we deal with several that are still on the 2017 code and a couple that are on older versions than that.
They can ignore the NEC if they want, but they are in violation of state law if they don't adopt a local ordinance that specifically overrides 250.25. But hey it's Texas, "NEC? We don't need no stinkin' NEC!"That said, there are several that have adopted the 2020 code and still want N and G isolated in the PV disco.
To a cursory reading it looks to me that it hinges on whether or not a supply side PV interconnection is considered a service as defined by the NEC. But you're not going to trap me into defending the AHJs' interpretations of the NEC.250.25
They can ignore the NEC if they want, but they are in violation of state law if they don't adopt a local ordinance that specifically overrides 250.25. But hey it's Texas, "NEC? We don't need no stinkin' NEC!"![]()
It doesn't. 250.24 applies to service disconnects. 250.25 applies to anything anyone tries to say is not a service disconnect, and refers back to 250.24, essentially requiring they be treated the same.To a cursory reading it looks to me that it hinges on whether or not a supply side PV interconnection is considered a service as defined by the NEC. ...
All I can say is "whatever"; that part of the code is a convoluted mess, IMO. I really don't care; I will design it the way the AHJ tells me to. It's not my job to play code nazi to the AHJ, especially in this case where it isn't a safety issue for people or equipment.It doesn't. 250.24 applies to service disconnects. 250.25 applies to anything anyone tries to say is not a service disconnect, and refers back to 250.24, essentially requiring they be treated the same.
Grounding is always a safety issue. I would not say, "the AHJ told me to do it wrong so I did it wrong, it's not my fault if something bad happened" but that's just me.All I can say is "whatever"; that part of the code is a convoluted mess, IMO. I really don't care; I will design it the way the AHJ tells me to. It's not my job to play code nazi to the AHJ, especially in this case where it isn't a safety issue for people or equipment.
In this case I don't agree, but although I know a lot I don't know everything. Can you tell me what could happen that would be a safety hazard when a line side PV interconnection is not treated as a service, i.e., ground and neutral are separated in the PV AC disco and an EGC is run back to the MDP from the inverter(s) through the disco?Grounding is always a safety issue. I would not say, "the AHJ told me to do it wrong so I did it wrong, it's not my fault if something bad happened" but that's just me.
You seem to be contradicting yourself here.personally if only considering lightning strike, i don't think . . . the system should be on its own ground seven feet from house ground if possible.
my belief is that everything (ground, neutral and both hots) were at the same potential, thus they survived.
no, i'm talking i think things should be wired and how my house was wired. my solar is connected to my only ground rod and my house is grounded to same ground rod, thus my solar is bonded to the neutral thru the neutral/ground bond in my two service panels. exactly as ggunn is describing above. so neutral and ground at same potential. ask my neighbors about their damages that are on the same transformer!You seem to be contradicting yourself here.![]()
I don't see how bonding ground to neutral in your PV AC disco would have made any difference. I am assuming that your PV system is supply side interconnected; if it were connected through a backfed breaker bonding N to G would have been a code violation.no, i'm talking i think things should be wired and how my house was wired. my solar is connected to my only ground rod and my house is grounded to same ground rod, thus my solar is bonded to the neutral thru the neutral/ground bond in my two service panels. exactly as ggunn is describing above. so neutral and ground at same potential. ask my neighbors about their damages that are on the same transformer!