Sajid khan
- Pakistan
In Seattle there are lots of vaults that are filled with water 24/365. They love it.
So No problem You mean.. We can leave it for years?
YesSo No problem You mean.. We can leave it for years?
Agreed, ours are wet for years. We just replaced some that was installed in the late 70’s. Been wet about all those years.So No problem You mean.. We can leave it for years?
replaced because it was 15kV and we went to 25kV for a conversion.
By the way, I designed systems of approx. 400 manholes -in each one of approx.10 power stations -and we run there about 300 medium voltage cables manufactured as per IEC 60502-2-and no more-no armour and only pvc outer jacket. Theoretically, in each manhole there is a sort of water sink and a system to extract the water, but I never saw it working. The first power station manhole system which I designed was in 1985 and the manholes are almost always full of water. I do not remember it was once a complaint. However, according the standard the cable has to be in less water.