ldtOLER1112
 - TAMPA, FLORIDA, USA
Is there anyway to change the input voltage on a VFD. I've got 120/208 and the VFD is 400 to 460 input
			Your best bet is to either replace the VFD or get a step up transformer. These days just getting any VFD is a chore so your best bet is probably a step up transformer. I would suggest a 3 phase 208 delta primary to 3 phase 480 wye secondary.Is there anyway to change the input voltage on a VFD. I've got 120/208 and the VFD is 400 to 460 input
The few times we had to change either 208 or 240 volts to 480 volts never used a Wye on the secondary if it was feeding a three phase drive or motor that only required 3 wires.Your best bet is to either replace the VFD or get a step up transformer. These days just getting any VFD is a chore so your best bet is probably a step up transformer. I would suggest a 3 phase 208 delta primary to 3 phase 480 wye secondary.
If you don't use a wye with the center grounded, you will have to make the 480 corner grounded or install ground detectors.The few times we had to change either 208 or 240 volts to 480 volts never used a Wye on the secondary if it was feeding a three phase drive or motor that only required 3 wires.