Parallel feeds

Status
Not open for further replies.
That's what I thought at first but I think he means six conduits with one set per.
I think that you're correct, I read it as 6 conductors per conduit. :rolleyes:
I would add two conduits and use 600 kcmil.
 
If you have 9x 300 kcmil per phase (3 of each phase in 3 conduits), then depending upon the neutral requirements you might be able to fit 2000A in the existing 3 conduits.

If you can get compact stranded Cu even better.


Jon
 
Shouldn’t the ground be sized to the individual raceways since each raceway has three 600mcm with a neutral thus a #2 copper
 
Ampacity of a single copper 300 is 320A. (This is the 90C ampacity, and if you use 90C conductors you can use that for derating).

9 * 320 * 0.7 = 2016

Jon
I didn't check the conduit fill but for 2000 amps the 300's would work.
 
I didn't check the conduit fill but for 2000 amps the 300's would work.

9 300's would fit, depending on conduit type.

The problem is if there remains sufficient room for EGC and neutral.

If the conduits were existing and changing them a major cost, then I'd try to get compact stranded Cu.

If this were initial design and conduit being selected then I would go with more conduits.

Jon
 
Shouldn’t the ground be sized to the individual raceways since each raceway has three 600mcm with a neutral thus a #2 copper
The equipment grounding conductor must be large enough to trip the overcurrent protective device. There is a reason that a 250 kcm conductor is required for 2000 amp overcurrent protective device. Each conduit must be capable of tripping that 2000 amp breaker.
 