mohsan514
- Saudi Arabia
I am facing issue with chiller , we have installed YORK chiller with Full load current of 1200 Amp. ,
Once we are running the chiller , main breaker from MDB is tripping dur to Ground Fault , the strangr thing is Chiller itself has Schneider Breaker and GF setting is at 300Amp , and upstream setting is 450 amp..
Also we disable the Ground fault protection from MDB breaker , chiller worked fine without any tripping.. And we monitor the Ground Fault current from MDB breaker it reaches to 600 Amp ... but chiller was working fine..
We called the experts from York and they confirmed that there is no issue in chiller site , they also Megger the main feeder cable it was OK...
What could be the reason of this??
Sent from my SM-A705FN using Tapatalk