I have 277v A-N, B-N, C-N
I have 480v A-B, B-C
I have 0V A-C
At MDP I have 277v all phase to ground and 480 across all phase to phase. This was a retrofit wire pull and has 4-4/0Al and 2/0 in a 2.5in pipe. Is it possible the wire was nicked or stretched enough on the pull in that would cause a break down? It worked for about a year. The neutral was not needed, but specced so it got pulled in also. I took neutral and made it the C phase and all is good. Any ideas here?
I have 480v A-B, B-C
I have 0V A-C
At MDP I have 277v all phase to ground and 480 across all phase to phase. This was a retrofit wire pull and has 4-4/0Al and 2/0 in a 2.5in pipe. Is it possible the wire was nicked or stretched enough on the pull in that would cause a break down? It worked for about a year. The neutral was not needed, but specced so it got pulled in also. I took neutral and made it the C phase and all is good. Any ideas here?