Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
generally you have a house panel for things that are shared and the electricity from the house panel is paid for by the landlord. I don't think this is a NEC requirement though.Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
See 210.25. Also see the Massachusetts amendment to that section.Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
I don't either, local rules are when this typically is an issue.generally you have a house panel for things that are shared and the electricity from the house panel is paid for by the landlord. I don't think this is a NEC requirement though.
See 210.25I don't either, local rules are when this typically is an issue.
Doesn't automatically mean you need a separate panel for "house" loads, only if there are "house" loads must they comply with that section.See 210.25
So what you're saying is that there is an NEC requirement for "house" loads to be supplied from equipment other than the equipment which supplies an individual dwelling unit or tenant space.Doesn't automatically mean you need a separate panel for "house" loads, only if there are "house" loads must they comply with that section.
What if owner stops paying utility bill or at least misses paying bill for whatever reason and the "house" gets disconnected?Unless management pays for power, the concern is that a tenant could leave or lose power and the common areas would become deenergized.
Yes, but OP didn't give enough details so the answer to his original question is "maybe".So what you're saying is that there is an NEC requirement for "house" loads to be supplied from equipment other than the equipment which supplies an individual dwelling unit or tenant space.
It really depends on the "lay out" of the multifamily dwelling.Is there a requirement in either the electrical or building code that states we have to install a common panel for a two or three family building?
The answer to the OP's question is "210.25"Yes, but OP didn't give enough details so the answer to his original question is "maybe".
210.25 Excellent! Thank you.
Then the tenants have to complain to their housing authority.What if owner stops paying utility bill or at least misses paying bill for whatever reason and the "house" gets disconnected?![]()