I'm looking for opinions on whether or not the rule of 6 applies to a situation I have. It is an Industrial facility where the utility is supplying 12.47KV. The line of demarcation is at a switchyard where, after the metering, it then feeds an isolation switch on the company side of the line of demarcation, with kirk key interlock to a main breaker located in company-owned 15 kV switchgear. There is one service, meaning one set of service conductors, leading from the isolation switch to the switchgear lineup that, as I said, first lands on the MCB at th 15 kV switchgear, which then supplies power to adjacent switchgear sections containing breakers that serve various buildings on the site. Does NEC 230.71 now limit the number of feeder breakers in this arrangement to 6? My take is that there is only one service in play and the MCB is a single point of service disconnect with the downstream breakers being feeder breakers, and the number of feeder breakers isn't limited to six by NEC 230. I am getting challenged on this by other engineers involved in the project.