Grounding electrodes

Status
Not open for further replies.
What type of electrode and what size are the service entrance conductors?
 
Table 250.66 goes off of the size of the conductors. If you don't have a metal underground water pipe and are using a ground rod, then you only need a #6 per 250.66(a)
 
What size grounding electrode do I need for a 300 amp service I have been told don't need bigger than #6 but I don't think that's accurate

Sent from my SM-A102U using Tapatalk
To "nit pick" a little, I think you are asking what size grounding electrode conductor (GEC). There are no sizes mentioned for electrodes themselves, only the conductors to them. As was mentioned, if using only a ground rod as an electrode, then #6 is all that is required. If using a Ufer, then #4 is required. There are a few other electrodes that require larger than #6. Of course, Table 266 is used to size them and some electrodes are exceptions to the table.
 
Last edited:
As long as the Grounding Electrode Conductor is terminated only on ground rod(s) (does not also go to any other electrode), a #6 is the largest you ever need regardless of the service size or the service conductor size.
 