480v fire

Status
Not open for further replies.

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
I was called out to a fire in a 3,000 amp 480 volt service that is fairly old and has no GFPE. 2 fuses on the primary side of 2 separate utility poles burned but not the main fuses in the panel.
 

Attachments

  • 480v service failure.jpg
    480v service failure.jpg
    101.2 KB · Views: 35
Is it solidly grounded wye system of over 150 volts but less than 1000 to ground? If not GFP wouldn't been required.
 
Is it solidly grounded wye system of over 150 volts but less than 1000 to ground? If not GFP wouldn't been required.
it was built before GFPE was required, it is a 277/480v
 