I'm not sure what has changed since I worked there in the 1970's-80's but I remember the following issues :
- Except for Local Law # 5 for high-rise buildings ALL regular fire alarm wiring had to be in rigid, galvanized conduit
- NO conduits can enter the TOP of any FA cabinet. That dates back to the days of the ACME FA systems. If there was a fire in a building and the FD was pumping water into the building via the siameese connection, they didn't want water coming down into the FA panel and shorting anything out.
- In conjunction with the FA system they had what was called a "strap key" system. That was in effect before they had reliable walkie-talkie communications. Basically it was a manual station that was operated in a stairwell by the insertion of a key the fireman had with him. If he wanted more water pumped into the sprinkler system he would activate a code to ring the gongs via the strap key to add water and another code to stop.
- You could not use a circuit breaker to feed an FA panel. You needed a 3-pole fused cut-out with a removable neutral (usually a piece of copper pipe). You had to TAP off the line side of the service switch with no more than 10' of galvanized conduit (1 std. length). From there it was 120/208 to the FA panel. One phase to operate the panel and another (JUST IN CASE) THEY LOST THE FIRST LEG). That was in effect before they had battery back-up.
- Electricians used to run # 10 solid even for the newer FA panels that drew about 1 amp (go figure).