- Chapel Hill, NC
- Retired Electrical Contractor
I get it but in one case you are using the street copper lines as a grounding electrode and the other case, where the copper is replaced outdoors, you are just bonding the copper pipes that could potentially get energized.The pipes are currently bonded, via the bonding jumper from the switchgear to the water meter. Once the copper pipe water mains in the building are replaced with CPVC, the water piping in the dwelling units will not longer be bonded. Hence having to add a (3/0) jumper along the CPVC piping, to bond all of the copper stubs running into the dwelling units.