PeterJ007
- Phoenix, AZ
- Electrical Engineer
I need some help understanding what is happening to one of the 2.5MVA power transformers at one of our solar project sites.
We have two, identical. hermetically sealed, mineral oil filled, 2.5MVA transformers, each fitted with a DMC protection relay. One transformer is functioning perfectly, the other is exhibiting the generation(?) of gas. The gas pressure builds up in the DMCR, forces the oil level in the DMCR below the oil-level trip threshold, and the transformer trips. Upon manually releasing the gas pressure in the DMCR, the oil level returns to its original level and the transformer can be operated again. This appears to happen about every four hours of operation.
We have had the mineral oil tested and no hydrocarbons or other contaminants have been found – which would indicate that there are no internal arcs causing the gas – so we are at something of a loss as to understand the source of the gas.
I just wondered if you had come across such a phenomenon on your travels and if so what the cause/solution might be?