Many years ago as an apprentice I saw this scenario on a job and it had a disastrous outcome. Now I'm face with nearly the same thing and don;t want the same results.
When I was an apprentice we were wiring a job at a commercial laundry. The main service was 277/480volt, the designer had designed the low voltage to be 120/208volt, which is the standard here. The dryers arrived and they were 230v (all three phase). The Journeyman I was working with connected the 230v dryers to the 208v circuit, telling me that 208 and 230 function the same phase to phase and it didn't matter. However, evidently that wasn't the case with this dryer that required a high leg. Two days later it caught fire and my boss had to buy the dryer. The problem was solved by installing a different transformer that supplied the correct voltage to the dryers.
Now, years later I'm faced with the same problem, except now, I'm the boss and I really don't want to buy a burned commercial dryer. My situation is different because I don't have 277/480v coming into the building, the service is 120/208v from the power company. I called the supply house and asked if they had a transformer with a 120/208 volt primary and a 230 volt secondary, they did, but is a special animal, a 230 volt Open-Delta that only outputs 230 volts.
I'm at a loss here and don't have the time or money for trial and error or experimentation, I have to get this right the first time or I'm sunk. Any advice would be appreciated.