reaplaypolo
- West Virginia
- Instructor
Hello,
I have few questions.
Q1) If The motor has 50HP and 65 FLC, Why Field disconnect rating -HP is 50HP. I think 65 HP instead of 50HP.
Q2) As I know, Motor Starter consists of Motor Contactor and Motor Overload Protection//
Q2-1) Can I assume that Motor controller is the same as Motor Starter or Disconnection SW?
Q2-2) Can we use the same symbol of Motor Starter and Motor Contactor?
Q3) To calculate on the Feeder Conductor Ampacity by using Table 310.15(B)(16), A Question has only gave us for 75 degree. How can we choose Cooper 75 degree from two 75 degree column of the table 310.15(B)(16) eventhough we have only given condition as 75 degree?
| Motor Field Disconnect | |||
| Field disconnect rating - current rating | 74.75 | A | FD Rating >= 1.15 FLC for single motor [430.110(A)]?? |
| Field disconnect rating - HP | 50.00 | hp | FD Rating >or = hp rating [430.110(A) Exception]?? |
| Feeder conductor base ampacity | 95.25 | A | Ampacity >= 1.25*(Imtr,max) + 1.00 *(sum Imtr,fla) + 1.25 * (sum Ires) [409.20] (This is a superset of [430.24]) |
| Feeder conductor temp derating | 1.00 | (Ambient Tem --> 30 deg C) 30 deg C => derating factor = 1.00 [Table 310.15(B)(2)(a) temp correction factors] | |
| Feeder conductor ampacity Allowing for temperature derating | 95.25 | A | Ampacity from table = Base ampacity / derating factor [Table 310.15(B)/ Table 310.15 (16)] |
| Feeder conductor multconductor derating. Derating for Number of conductors | 1.00 | [Table 310.15(B)(3)(a)] 3 cond (3 phase) => 1.00, 4-6 => 0.8, 7-9 => 0.70, 10-20 => 0.50, 21-30 => 0.45, 31-40 => 0.40, >=41 => 0.35 | |
| Feeder conductor ampacity Allowing for multiconductor derating | 95.25 | A | Ampacity from table = Base ampacity / derating factor [Table 310.15(B)/ Table 310.15 (16)] |
| Feeder conductor Sizing | 3 | awg | [Table 310.15(B)(16) - 75 deg C] and [240.4(D) ] (Formerly [Table 310.16]) Note [NEC 240.4(D)(1-7)] the following limits: 18 awg Cu<=7A, 16 awg Cu<=10A, 14 awg Cu<=15A, 12 awg Cu<=20A, 10 awg Cu<=30A. Also see [430.53(D)] 75 dec C connectors assumed. 75 deg C used for all conductors [110.14(C)] |